Stricter yes like NEC, and for good reason. Easy to hop out of an RV or EV on fire. Not so easy on a plane or boat.Wire size calculations in aircraft get even crazier.
What many on-line calculators fail to take into consideration is SHORT distances. They assume lengths of 15 feet or longer will be used. Many do not put a Fail - Safe check built-in to see if the wire can safely handle the current or not.
For example enter in 2-feet, 50 amps, and 3% loss and many sites will come back with 12 or 10 AWG. If you have experience in electrical power know immediately that is dangerous. Sure a 2-feet run of 12 AWG will have the resistance low enough so that the wire only losses .36 volts with 50 amps flowing. Trouble is it becomes a Space Heater and burns the insulation off the wire. You would know instinctively and from experience the minimum safe wire size for 50 amps using 105 degree Insulation is 6 AWG.
Now some on-line sites are aware of this and have put in the Sanity Check. Some learned the hard way when they got sued and had to replace someones home because they are incompetent pretending to be experts. I know this for fact because it happened on a Forum I moderate. Yes this forum can be sued giving inaccurate or false information.
So remember this. Wire size is based on the OCPD (Over Current Protection Device like a fuse or breaker) feeding the wire. If you have a 20-amp circuit, the minimum wire size must be 14 AWG or larger. Does not matter if the circuit only caries 1 amp. A OCPD only has one purpose and one purpose only, and that is to protect the wire connected to the LOAD side. It has no other purpose. They are not there or capable of preventing electrical shock or protect the utilization equipment. Only the wire and nothing else. That 3000 watt Inverter at 12 volts requires a 300 amp fuse and a minimum 250 MCM (aka 4/0) copper cable. Voltage drop of a short 10 feet is of no concern operating at 12 volts. On the same lines anything over say 15 feet because a huge concern using toy voltages like 12 and 24 volts. You could find yourself needing multiple parallel pairs of 750 MCM. Use a higher voltage and all that goes away or a lot further out before it becomes a problem.
Low Voltage + High Power = Fire Hazard. Anything over 500 watts is high power for 12 volts.