AC motor selection differs from DC motor selection because AC controllers may require a matching motor. In fact, most AC motors marketed for EVs come with a controller. These controllers often (but not always) include a built-in charger and DC-DC converter. Below is a list of AC motor and speed controller combinations.
Industrial VFDs (Variable Frequency Drives) usually have a smart "learning" feature to configure itself for a particular motor, and can therefore be used almost universally with 3 phase induction motors and in some case permanent magnet synchonous (BLDC) motors.
Some parameters may need to be entered such as:
Base voltage, base frequency, nameplate RPM, max speed, max current, magnetising current, number of poles, encoder pulses per rev, overload rating, and Star or Delta connection. This will allow the VFD to run in a very basic Volts/Hz mode, meaning it can control speed but not torque.
To run in a torque controlling mode, the VFD needs to "learn" (sometimes called "Auto tune") the motor characteristics. The VFD simply spins up the motor with no load on the shaft and generates an electrical model of the motor at various RPMs. Some VFD's can do these measurements on the fly as the motor is running, eliminating the need for Auto tuning. Sensorless vector mode uses Back EMF from the motor to measure motor speed, and control torque. Closed Loop Vector mode uses an Encoder to measure motor speed. The encoder has better accuracy, and enables finer control of speed and torque.
A VFD used in an EV must support vector control (torque control), and have access to the DC bus for connecting to the battery pack. Be aware that the VFD manufacturer may not warranty their product if used in an EV.
Motor | Controller | Continuous Power (hp/kW) | Peak Power (hp/kW) | Peak Torque (ft-lbs/N-m) | Weight(lbs)/ Mass(Kg) | Diameter (In/Cm) | Length (Inc/Cm) | Voltage Range (rms) | Max rpm | Link to Manufacturer or Retailer |
AC Propulsion T-zero | T-zero | ?/? | 268/? | ?/? | 110/50 | 12in/305mm | 15in/381mm | ?/? | 13,000 | AC Propulsion |
AC Propulsion AC-150 | AC 150 | ?/? | 200/? | 165/225 | 110/50 | | | 240/450 | 12,000 | AC Propulsion |
Siemens 1PV5135-4WS28 | ? | 90hp/67kW | 160hp/120kW | 317/430 | 200/90 | 9.65in/245mm | 16.7in/425mm | 460V | 10,000 | Siemens |
Solectria AC24 | DMOC445 | 18.77/[email protected] | 49.6hp/37kw | 57.66/78.19 | 83.6/38.0 | 9.45/24.0 | 15.55/39.5 | ? | 12,000 | Electroauto |
Solectria AC55 | DMOC445 | 46/[email protected] | 63.0hp/47kw | 105/142 | 234.35/? | 13.5/? | 16.4/? | ?/? | 8,000 | Electroauto |
ABB 3GAA 131 003-**E | Industrial VSD | 15hp/11kW | 50hp/37.5kW | 92/125 | 115/52 | 10.3in/260mm | 14.5in/367mm | 220V-690V | 6,000 | ABB |
ABB 3GAA 131 315-**E | Industrial VSD | 15hp/11kW | 67hp/50kW | 122/165 | 170/77 | 10.3in/260mm | 18.5in/470mm | 220V-690V | 6,000 | ABB |
ABB 3GAA 131 316-**E | Industrial VSD | 20hp/15kW | 80hp/60kW | 147/200 | 178/81 | 10.3in/260mm | 18.5in/470mm | 220V-690V | 6,000 | ABB |
ABB 3GAA 131 317-**E | Industrial VSD | 25hp/18.5kW | 94hp/70kW | 203/275 | 210/95 | 10.3in/260mm | 18.5in/470mm | 220V-690V | 6,000 | ABB |
ABB 3GAA 132 004-**E | Industrial VSD | 12.3hp/9.2kW | 34.5hp/26kW | 125/170 | 130/59 | 10.3in/260mm | 14.5in/367mm | 220V-690V | 4,500 | ABB |
ABB 3GAA 132 315-**E | Industrial VSD | 15hp/11kW | 52hp/38.5kW | 192/260 | 183/83 | 10.3in/260mm | 18.5in/470mm | 220V-690V | 4,500 | ABB |
ABB 3GAA 132 316-**E | Industrial VSD | 20hp/15kW | 80hp/60kW | 288/390 | 203/92 | 10.3in/260mm | 18.5in/470mm | 220V-690V | 4,500 | ABB |
Notes For Reading Chart:
All voltages are given in RMS voltage. If you wish to calculate the battery pack voltage necessary, simply multiply the desired or stated RMS value by 1.41 or sqrt(2).
Take the power figures as a guideline only. Most induction motors may be overpowered above their base speed by using a higher pack voltage, extending the constant torque region.
Remember, power (Watts) is the product of torque (Nm) multiplied by speed (rads/s or RPM/9.55). Power figures are stated for the motor's base speed, not the maximum speed.
Notes for Adding Motors:
If you are not comfortable in editing this wiki then post the information in the forums so they can be transferred to here.
These motors are ranked according to their power at their
maximum voltage. Statistics would vary using smaller voltages.
I have sourced the information for the Siemens AC induction motor from
http://www.metricmind.com/audi/main.htm
For imperial and metric conversions just google a converter.
Hope you find this useful